Hmmm... well keep in mind that when the motor reverses there is a strong
inrush of initial current.... it's not that unusual for a vacuum cleaner to
dim all the lights for a moment when it first starts, and there's a pretty
strong analogy between that and your washer motor reversing. Actually your
motor may not be reversing, or even start-stopping, but the motor is
stressed a lot when the reversing gears click back and forth. You might also
want to investigate the condtion of the motor starting circuit, IE the
start/run caps and/or centrifugal or voltage sensitive switch that cuts out
the starter cap.

That having been said, I've never heard of a washer doing that. Because the
washer is on a dedicated circuit, the voltage drop you are getting is
somewhere between the panel and, well, your utility company. Perhaps the
connection to your meter is loose, the service drop is undersized, or you
are a long way from the nearest transformer. Perhaps the sliding contacts of
the meter itself are corroded. Unfortunately you can rarely diagnose these
problems yourself because the meter box is sealed. If your meter box is
separated from your panel (like mine) you can certainly make sure the
connection to the panel is tight and of sufficient gauge. If the effect is
pretty dramatic the power company might not mind taking a look at their
side, if there is a point of high resistance it could represent a fire
hazard, and in any case excessive voltage drop is criminally inefficient
(against code). Have you ever noticed the box or perhaps the main breaker
getting hot? If I were you I might measure the voltage at the breaker panel
with eveything in the house turned off, then measure again with everything
turned on: as much load as you can get, waffle irons space heaters all the
lights etc. I believe there is a go/no-go criterion for the maximum drop you
should measure, but I don't know what it is (NEC should say). If you want to
be a bit more detailed, calculate the actual high load you are placing,
measure the drop, and then multiply the drop by the ratio of the main
breaker size to the load. For example if you calculate you are drawing 50
amps and the drop is 6 volts, and you have a 200 amp main breaker, it's
reasonable to assume you'd get a 24 volt drop at 200 amps draw, which I
think is clearly too much. One could argue that despite the fact that you
have a 200 amp breaker, the anticipated load would not be 200 amps therefore
the power company might thumb their nose at your calculations, but the
counter-argument (that the service to a 200 amp breaker should be sized for
200 amps) probably prevails in code. You should do your measurements on each
side of the split phase, understand the pattern of the bars behind the
breakers, and probably add and shed loads by flipping the breakers
themselves. If you're carefull in your calculations (or move your appliances
so that they're all on one side, then the other), you may find that one side
has a much higher drop/resistance than the other side, which would almost
certainly indicate a problem. Finally, you might try leaving the high load
connected for 30 minutes or so (each side) while checking the various
components for hot spots: and be prepared for an electrical fire anywhere
between your breaker box and the power co's transformer. Do these
experiments in the order presented, if the voltage drop in the first
experiment is significant don't try the second. My guess is, if you discover
excessive drop and report it, the power co won't charge to inspect: but if
they determine your feed is undersized and must be replaced they will
probably charge for that.

-Jeff

"Tom Haley" <haley-tom@xxxxxxxxxxx> wrote in message
news:Je6dna_8hvS8rHjYnZ2dnUVZ_rylnZ2d@xxxxxxxxxxxxxx
Continuously.
The service is 240v centertapped.
Neutral is good and well grounded. Good 120V reference to each leg.
Branch circuit is a rated 20A with 12 AWG copper conductors. It is a
dedicated circuit with no other loads other than the washer.
Circuit breaker is sized appropriately
Total length of branch circuit conductors is less than 40 feet.
The cycle of the flickering lights appears to coincide with the reversal
of
the agitator (1-2 seconds)
Connections at the panel and the receptacle are tight.
I haven't measured the actual current draw of the motor. That may be
worthwhile.
<hrhofmann@xxxxxxx> wrote in message
news:1172637146.206328.85920@xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx
On Feb 25, 2:27 pm, "Tom Haley" <haley-...@xxxxxxxxxxx> wrote:
I recently noticed that all of the lights in my home flicker from time
to
time.
I have isolated it to those times when my 120 VAC automatic washing
machine
is in its agitator cycle.
Is this a common problem?
Are there in-line filters available that can reduce this effect?

Do the lights flicker just once each time the cycle is started, or
continuously? What level of service do you have, 120V or 240V, and at
what amperage? It is not normal for a washing machine motor to draw
enough current to make the lights flicker in a house with adequate
wiring. It could be a badly grounded neutral, or undersized
conductors. Are you familiar with how a house is fed 240V
centertapped with the center tap being the neutral? Do all the lights
get brighter, dimmer, or do some circuits get brighter and some
dimmer?

H. R. (Bob) Hofmann






.



Relevant Pages

  • Re: New motor wiring problem.
    ... 115/220 22/11 amps pre wired for 115. ... double checked the diagram b2b, w2w, green to the grounding screw. ... It is on a 20 amp breaker off my sub panel on #12 wire. ... the box is fine that didn't pop but the one on the motor does. ...
    (rec.woodworking)
  • Re: New motor wiring problem.
    ... 115/220 22/11 amps pre wired for 115. ... double checked the diagram b2b, w2w, green to the grounding screw. ... It is on a 20 amp breaker off my sub panel on #12 wire. ... the box is fine that didn't pop but the one on the motor does. ...
    (rec.woodworking)
  • Re: How to mortar a whirlpool tub?
    ... area is much less than the overall base area, ... separate ground for the motor assembly directly from the panel. ... you should use a 20A breaker. ... mmm - the motor is rated for 15 amps calling for a 15 amp circuit. ...
    (alt.home.repair)
  • Re: OT - electric motor issue
    ... Often when the compressor tries to start again (triggered by ... By rotating the motor by hand ... prior to resetting the breaker, ... The starting amps are much higher than the full load amps, ...
    (sci.electronics.repair)
  • Re: Ampere Turn in Electromagnet
    ... soft iron no bigger than a model train motor and play electromagnets. ... can it possible to know ampere turns of this electromagnet. ... Watts = Volts * Amps, so half voltage needs double amps for the same power. ... Hence copper is used for its minimal resistance ...
    (sci.physics)