Re: Battery capacity



Right,in the future I will be looking at resting voltage for the
remaining battery capacity. That brings the batteries closer to their
AH specs.

Thanks,

Larry


Dave Martindale wrote:
"larry.greenwood@xxxxxxxxxxxxxxx" <lgreenwood@xxxxxxx> writes:
Interesting....I have noticed that when I turn off the load the voltage
go up a couple of percentage points, ie, a load voltage of 12.2 volts
goes up to 12.4 when I turn off the load. Is that what you are talking
about?

The voltage will rise a bit instantly when you remove the load, due to
the IR drop through the batteries' internal resistance being removed.
Then, as you leave the batteries for 24 hours, the voltage will likely
rise some more as things settle down in the battery.

Then you may find that you're still well above 50% charge, because the
table of voltage vs. capacity you are using is probably resting
voltage.

Dave

.



Relevant Pages

  • Re: AC to DC 65+ volts 60 amp Power Supply Plans?
    ... inverter section (where all that irritating pass-through-the-generator ... I'm using Inverter #2 only to charge the batteries right now. ... So long as the diodes are not overly low voltage, ...
    (sci.electronics.design)
  • Re: Solar-hydrogen home power system?
    ... > The down side may have you consider batteries instead. ... > The biggy for you will be that the voltage is not constant. ... you will need a switcher that is tailored for caps. ... To control a motor of any type efficiently, you really need some kind of ...
    (sci.energy.hydrogen)
  • Re: Solar-hydrogen home power system?
    ... > The down side may have you consider batteries instead. ... > The biggy for you will be that the voltage is not constant. ... you will need a switcher that is tailored for caps. ... To control a motor of any type efficiently, you really need some kind of ...
    (sci.energy)
  • Re: battery box supplying 4 different voltages?
    ... On other bots I've tried it both ways, and did indeed find that it was easier to just have separate motor and logic batteries. ... Star or single-point grounding with the common point as close to the battery negative or bulk filtering capacitors as possible will help. ... should have eight conductors on this bus, rather than five, so that each voltage can have its own ground line. ... If you think about power distribution buses without capacitors, short term heavy loads will require the heavy load current be supplied from the battery. ...
    (comp.robotics.misc)
  • Re: 3-phase AC motor control for battery-electric vehicle
    ... which means a 600v dc bus so lots of batteries as well. ... a few motors for low voltage. ... motor VAC rating, so a 208/240 VAC motor would require less batteries (380 ... controller, but the high voltage inverter option uses standard components. ...