- From: Sam E <no.email@xxxxxxxxxxx>
- Date: Sun, 25 Oct 2009 20:50:27 -0500
[snip]
You have a SERIES circuit (considering that the neutral is effectively
disconnected).
[snip]
Wrong. The neutral is "effectively disconnected" *only* if the loads on the
two legs are exactly the same.
Which they are (either in the 200A+200A example or the 1A+1A one).
The two legs function as two parallel circuits
with respect to 120V loads.
In a parallel circuit BOTH ends of the loads are connected together
(or at least to identical voltages). Neither is true here.
Obviously they are indeed in series WRT 240V
loads.
Strangely, I get the idea that you actually know this stuff.
In this 200A service there are THREE current-carrying conductors.
Each of these conductors is of the proper size to carry 200A. OK so
far?
You say (when this service is fully loaded) that two of these
conductors is carrying 200A (for a total of 400A, as you say).
Then where is that 400A going? The only remaining conductor is the
neutral, a big enough conductor for 200A (yes, this 400A was at 120V
but current is still current and voltage doesn't change the
conductor's current capacity).
Somehow I'm imagining a bridge that can handle 200 cars per minute,
but that can be 400 if half the cars are blue :-)
.
- Follow-Ups:
- Re: Load capacity of 200-amp panel
- From: Doug Miller
- Re: Load capacity of 200-amp panel
- References:
- Re: Load capacity of 200-amp panel
- From: trader4
- Re: Load capacity of 200-amp panel
- From: Doug Miller
- Re: Load capacity of 200-amp panel
- From: trader4
- Re: Load capacity of 200-amp panel
- From: Doug Miller
- Re: Load capacity of 200-amp panel
- From: trader4
- Re: Load capacity of 200-amp panel
- From: Doug Miller
- Re: Load capacity of 200-amp panel
- From: Sam E
- Re: Load capacity of 200-amp panel
- From: Doug Miller
- Re: Load capacity of 200-amp panel
- Prev by Date: Re: Load capacity of 200-amp panel
- Next by Date: Re: DIY incubator?
- Previous by thread: Re: Load capacity of 200-amp panel
- Next by thread: Re: Load capacity of 200-amp panel
- Index(es):
Relevant Pages
|