Re: help for troubleshooting




"greenhvactech" <candyharrykids_at_yahoo_dot_com@xxxxxxx> wrote in message
news:497360a8$0$5248$6c36adad@xxxxxxxxxxxxxxxxxxxxxxxx

I have a 2 ton amana that the condenser is not powering up but the
contacter and capaceter and 24 v transformer is been replaced I have power
to t-stat but not to the condenser can anyone help i think the troble is
in the wiring
-------------------------------------




##-----------------------------------------------##
Delivered via http://www.thestuccocompany.com/
Building Construction and Maintenance Forum
Web and RSS access to your favorite newsgroup -
alt.home.repair - 335612 messages and counting!
##-----------------------------------------------##

Your description doesn't give any helpful information. The condenser is not
powering up, but some parts have been replaced. Were the parts bad? You need
to check the contactor at the condenser. First see if it has 240 volts on
the line side. If not check the feeder, disconnect, and circuit breaker
feeding the unit. If you do have 240 volts at the line side of the
contactor, check for 24 volts at the coil terminals. if you do have 24 volts
at the coil, and the contactor is not pulling in, you have a bad contactor.
If you do have 24 volts at the coil and the contactor is pulling in, there
is a problem with the condenser motor. If you don't have 24 volts at the
contactor coil, you need to trace the low voltage cable back to the air
handler and find out why


.



Relevant Pages

  • Re: My $45 homemade 10 HP phase converter is WORKING!!!
    ... the contactor does drop out when the 240 ... This just means that you've wired it to a standard switch. ... that when the contactor is closed it provides itself the coil voltage. ...
    (rec.crafts.metalworking)
  • Re: Air conditioner contactor snubber.
    ... I don't think most thermostats are capable of driving a motor contactor, ... 24 volt AC coil and something like 5 or 10 amp contacts. ...
    (sci.electronics.basics)
  • Re: Master contactor question
    ... Does the coil resistance change much as the contactor wears out? ... good conductor so they will heat up and oxidize even faster. ...
    (rec.aviation.homebuilt)
  • Re: Master contactor question
    ... If you had no contactor and had instead a big switch on the panel, ... you have a large wire coming into the cockpit. ... The coil current is an amp or so. ...
    (rec.aviation.homebuilt)
  • Re: Three phase switch for single phase?
    ... A contactor is a device that engages contacts by means of a mechanical ... When power is applied to the coil, ... very quickly and such contactors can be controlled with tiny switches, ...
    (rec.crafts.metalworking)

Loading