Re: Any way to "measure" wire gauge in power cord?
- From: davem@xxxxxxxxx (Dave Martindale)
- Date: Fri, 5 Sep 2008 20:27:38 +0000 (UTC)
"Ralph Mowery" <rmowery28146@xxxxxxxxxxxxx> writes:
"Boden" <Boden@xxxxxxxxxxxxx> wrote in message
Measure the resistance. 14 gauge is 60% higher than #12 so it should be
easy to do.
Almost no home owner will have a meter that can measuer the differance in
the resistance of 10 feet of # 12 and # 14 wire. It would be the differance
of about .0159 and .0252 ohms for 10 feet.
Good thought , but impractical for almost every one.
It would almost take lab grade equipment to do that.
Few people have a single meter with a sufficiently low-range ohms scale
at home, but you can still do it with a bit of ingenuity. If you pass
a constant current through the wire, you get a voltage across the ends
that is proportional to the wire resistance, and many DMMs (even some
of the cheapest ones) have a 200 mV scale. For example, with a 1 A
current source, the two 10-foot pieces of wire in the example above
would have a voltage drop of 16 and 25 mV, enough to be told
apart by a DMM on even a 2 V range.
The most convenient current source for this would be a lab supply with a
few amps of output and a constant-current mode. But a 6 V or 12 V
battery (or power supply) plus the appropriate resistor to give an amp
or two of current will also work. Just measure the actual current and
the voltage across the wire and divide to get resistance. The resistor
needed will be a few ohms, so inserting a meter set to its 10 A range
will have negligible effect on the current.
I once had a problem figuring out how a particular circuit was wired in
a previous home. I opened the breaker, then connected a lab supply set
to 1 A constant current mode to one outlet that I thought was probably
near one end of the string. I shorted hot to neutral at another outlet
that I though was near the other end. Then I measured the voltage at
all of the other outlets on that circuit. There was an easily
measurable voltage drop (tens of mV) between boxes along the circuit,
so I could tell what sequence they were wired in, and where an outlet
was fed from a "tee" along the main path. (It turned out that some
previous owner had routed the circuit through a junction box that was
completely buried inside a wall, with no access from any side).
Note that this method only works when power is completely disconnected
from the house panel. If you try it on an energized circuit, you'll
probably destroy your power supply!
Dave
.
- Follow-Ups:
- Re: Any way to "measure" wire gauge in power cord?
- From: AZ Nomad
- Re: Any way to "measure" wire gauge in power cord?
- References:
- Re: Any way to "measure" wire gauge in power cord?
- From: Boden
- Re: Any way to "measure" wire gauge in power cord?
- From: Ralph Mowery
- Re: Any way to "measure" wire gauge in power cord?
- Prev by Date: Re: Any good contractors?
- Next by Date: Re: Any good contractors?
- Previous by thread: Re: Any way to "measure" wire gauge in power cord?
- Next by thread: Re: Any way to "measure" wire gauge in power cord?
- Index(es):
Relevant Pages
|
Loading