Pete C. wrote:
HeyBub wrote:trader4@xxxxxxxxxxxxx wrote:On Apr 17, 3:50 pm, "HeyBub" <hey...@xxxxxxxxxxxxxxx> wrote:
You're right, of course. MOV are classified as "electronic" components. ButIntermatic surge protectors do not use MOVs - they are electronic.What is this claim based on? If they don't use MOV's what exactly
do they use? Also, this would seem to imply that MOV's are not
considered electronic components, but I believe by any reasonable
definition, they are electronic components.
metallic-oxide-varistors work like reverse fuses: they short their terminals
together. And, like fuses, they (usually) only work once with no indication
(other than sometimes smoke) that they won't work again.
MOVs will continue to work indefinitely if their rated clamping current
isn't exceeded, so they will readily clamp on the modest surges seen
every day. The mega surges from a really close lightning strike or a
tree branch dropping the primaries into the secondaries is what will
cause the MOV to self destruct and usually trip the circuit breaker in
the process thereby sacrificing itself to save the stuff downstream of
it.
While MOVs are good with very short duration surges, dropping a primary wire onto secondaries will rapidly destroy a MOV as you describe. Then protection is gone.
UL requires thermal disconnects for failing MOVs. The specs from trader4 include “200k AIC Surge Rated Fuses” which indicate that suppressor can be used on in a panel with an available fault current (not surge related) of 200,000A. The suppressor may also trip a circuit breaker, but protection should be internal.
I believe the maximum likely surge current on one of the hot service wires is 10,000A based on a very strong 100,000A surge hitting the high voltage wire on the pole behind your house. The spec from trader4 is 40,000A per wire for that suppressor, which is well beyond what is likely.
MOVs also have an energy (Joule) rating, which is cumulative. The 40,000A rating goes with a very high Joule rating, which means the suppressor can take many hits. If a MOV had a 1000J rating, it is for a single surge. If the individual hits were much smaller, like 100J, the cumulative rating is much higher than 1000J. When the energy rating is exceeded, the MOV starts to conduct at lower voltages, eventually conducting at ‘normal’ voltages and failing in thermal runaway.
Without a service panel suppressor, there will be arc over to panel ground at about 6,000V. After it is established, the arc voltage will be hundreds of volts. That dumps most of the surge energy to earth. For plug-in suppressors, the impedance of the branch circuit wiring greatly limits the current, and thus the energy, that can reach the suppressor. Combined with arc over, the energy that can reach a plug-in suppressor is surprisingly small (unless the branch circuit is very short).
--
bud--
.
- References:
- Intermatic Whole House Surge Protector ?
- From: Robert11
- Re: Intermatic Whole House Surge Protector ?
- From: HeyBub
- Re: Intermatic Whole House Surge Protector ?
- From: trader4
- Re: Intermatic Whole House Surge Protector ?
- From: HeyBub
- Re: Intermatic Whole House Surge Protector ?
- From: Pete C.
- Intermatic Whole House Surge Protector ?
- Prev by Date: Re: Paint For Inside Microwave Oven
- Next by Date: The J12 watch series is made up of: the Ceramic Series, the Joaillerie Series, the Superleggera Series and the Special Edition Series.
- Previous by thread: Re: Intermatic Whole House Surge Protector ?
- Next by thread: Re: Intermatic Whole House Surge Protector ?
- Index(es):
Relevant Pages
|