Re: A/C compressor won't shut off



Zyp wrote:
Meat Plow wrote:
On Mon, 20 Aug 2007 07:58:23 -0500, Peabody wrote:

Everything seems to be working fine, but then when the thermostat
trips off, and the furnace blower fan turns off as it should, the
compressor outside keeps running. If I take the cover off the
electrical section and give it a sharp rap, it lets go and turns
off. So it appears it has to be a relay that's not letting go.

Well, all I can see in there is the main contactor, which has pretty
pitted contacts, and the hard-start relay. I was planning on
replacing the contactor, but wondered if it could possibly be the
start relay that's not letting go.


Contactor relay.

Replace the contactor, wash the condenser coil. It's likely dirty,
causing unsually high amperage draw, heating the contractor contacts
and 'welding' them together. Also, replace the air filter to limit
long run times.

I would agree with changing the contactor but a high head would not cause
the contacts to burn and pit.

I would think worn out contacts and check your hard start cap. to see if you
spot any damage. If so replace the relay and cap.

I also agree that you should wash your coils and change your air filter.
--
Moe Jones
HVAC Service Technician
Energy Equalizers Inc.
Houston, Texas
www.EnergyEqualizers.com


.



Relevant Pages

  • Re: A/C compressor wont shut off
    ... trips off, and the furnace blower fan turns off as it should, the ... So it appears it has to be a relay that's not letting go. ... Well, all I can see in there is the main contactor, which has pretty ...
    (alt.home.repair)
  • Re: relays
    ... wiping compared to relays with wiping. ... There exists an object that is a relay and has wiping contacts. ... There exists an object that is a contactor and lacks wiping contacts. ... A device by which contacts in one circuit are operated ...
    (sci.electronics.design)
  • Re: relays
    ... wiping compared to relays with wiping. ... There exists an object that is a relay and has wiping contacts. ... There exists an object that is a contactor and lacks wiping contacts. ... A device by which contacts in one circuit are operated ...
    (sci.electronics.design)
  • Re: A/C Compressor Relay will not close
    ... 24 VAC at the contactor, and it doesn't pull in, the coil is NG. ... The tech decided that the circuit board was not working and physically ... I found that the thermostat had been ... relay does not close. ...
    (alt.home.repair)