Re: #6 or #4 wire in 3/4 inch thinwall?



On Aug 6, 3:02 pm, Speedy Jim <vo...@xxxxxxx> wrote:
RickH wrote:
On Aug 6, 2:11 pm, RickH <passp...@xxxxxxxxxxxxxxxxxxxxx> wrote:

On Aug 6, 1:34 pm, Speedy Jim <vo...@xxxxxxx> wrote:

RickH wrote:

I need to add a sub-panel about 40 feet away from my main panel. The
previous owner left an empty 3/4 inch run of conduit in case anyone
wanted to add a sub-panel to the other side of the house (for an
addition) (conduit runs interior sub-panel will be interior). Now is
the time for that addition. I would like to run #6 wire to the sub
panel because one of the new branch circuits will have a 30 amp steam
unit for the bath. Ideally I'd like to run #4 wire even if I can.
The 40 foot run only has one 90 degree bend right at the main panel
and I could put a large pull box at the other end prior to bending
into the sub panel with any size pipe I want.

Can I get three #4's in 3/4 inch thinwall or must I use #6? My
intention was to undersize the feed breaker in the main panel to
accomodate whatever wire I can get into this pipe.

Must use #6 (THHN); 3/4 won't accept #4.

4 #6 allowed.
I would pull 3 #6 plus 1 #8 (or #10) Grn Equip Ground.

60 Amp breaker. (Technically, could be a 70)

With the steam unit (Line-to-Line), it might be possible
to use a reduced Neutral size for the feeder, but that may be
making things too complicated...

Jim- Hide quoted text -

- Show quoted text -

Thanks

The steam unit outlet will come off one of the sub panel branch
breakers (30A/220V GFCI) thats no problem as that outlet is not yet
roughed in. The remainder of the branch breakers in the new sub panel
will be for misc lights and outlets in the new addition. 60 amps
total to the sub panel via 3 #6 should be plenty plus a #8 or 10 bare
safety ground wire. (considering my entire first home had 60 amps
total service)

Then you would suggest re-grounding the new sub panel with the bare
wire (in addition to the natural conduit-created ground)? Just to
make sure it has a good tight ground? I'm assuming one should not re-
bind the neutral again in any sub panel, is this true? FYI I'm having
an apprentice electrician do the work (my nephew) I just like to know
what's going on capacity-wise.- Hide quoted text -

- Show quoted text -

Meant to say:

I'm assuming one should not re-bind the neutral to ground again in any
sub panel, is this true? Should the neutral-to-ground binding only
occur once in a house (at the meter or main panel)? No matter how
many sub-panels you have.

Right you are. The new sub-panel may come with a Bonding
screw intended to bond the Neutral bar to the enclosure/box.
Throw the screw away. :-)

If the panel doesn't come with one, you will need an
accessory Grounding bar so that the bare gound wires (Romex)
can be terminated on it, rather than on the Neutral bar.- Hide quoted text -

- Show quoted text -

Thanks Jim,

Thats what I thought, re-binding a neutral in a sub panel would make
the ground wire from the main panel into a normal-condition load
carrier. And it is my understanding that safety ground must never
carry a load in normal-condition, rather only when the connected
device has a fault.


.



Relevant Pages

  • Re: #6 or #4 wire in 3/4 inch thinwall?
    ... Ideally I'd like to run #4 wire even if I can. ... The 40 foot run only has one 90 degree bend right at the main panel ... The steam unit outlet will come off one of the sub panel branch ... Should the neutral-to-ground binding only ...
    (alt.home.repair)
  • Re: #6 or #4 wire in 3/4 inch thinwall?
    ... addition) (conduit runs interior sub-panel will be interior). ... Ideally I'd like to run #4 wire even if I can. ... The steam unit outlet will come off one of the sub panel branch ... Should the neutral-to-ground binding only ...
    (alt.home.repair)
  • Re: Carbon dioxide bike tyre inflation (was Re: That was dumb..)
    ... Then there's the spring push-in style for solid wire only. ... We turned off the breaker and took it apart to find a *very* loose ... whole panel if it's not up to current code. ... Will they install the other two fuses (and a three-phase ...
    (alt.sysadmin.recovery)
  • Re: Household sub-panel neutral isolated from ground
    ... at the sub-panel AND the neutral and ground are still short to each ... low voltage to put between a person and the dangerous voltage available within the system. ... At the point where the neutral is grounded, (bonded to the safety ground conductor) the impedance of the ground electrode must be low enough that expected current through this path do not produce dangerous safety ground conductor voltage with respect to local Earth. ... If the neutral conductor between the main panel and the were to become high resistance, and the ground and neutral were bonded at the sub-panel, Then the safety ground conductor at the sub-panel would be expected to have a voltage proportional to load current. ...
    (sci.electronics.design)
  • Re: Breaker Panel Mess
    ... >Terminal strips to land the 'Field' wiring is a great way to wire a panel. ... >The wires from the breakers to the terminal strips can be bundled neatly. ...
    (rec.boats.electronics)

Loading