Re: #6 or #4 wire in 3/4 inch thinwall?



RickH wrote:

I need to add a sub-panel about 40 feet away from my main panel. The
previous owner left an empty 3/4 inch run of conduit in case anyone
wanted to add a sub-panel to the other side of the house (for an
addition) (conduit runs interior sub-panel will be interior). Now is
the time for that addition. I would like to run #6 wire to the sub
panel because one of the new branch circuits will have a 30 amp steam
unit for the bath. Ideally I'd like to run #4 wire even if I can.
The 40 foot run only has one 90 degree bend right at the main panel
and I could put a large pull box at the other end prior to bending
into the sub panel with any size pipe I want.

Can I get three #4's in 3/4 inch thinwall or must I use #6? My
intention was to undersize the feed breaker in the main panel to
accomodate whatever wire I can get into this pipe.


Must use #6 (THHN); 3/4 won't accept #4.

4 #6 allowed.
I would pull 3 #6 plus 1 #8 (or #10) Grn Equip Ground.

60 Amp breaker. (Technically, could be a 70)

With the steam unit (Line-to-Line), it might be possible
to use a reduced Neutral size for the feeder, but that may be
making things too complicated...

Jim
.



Relevant Pages

  • #6 or #4 wire in 3/4 inch thinwall?
    ... I need to add a sub-panel about 40 feet away from my main panel. ... previous owner left an empty 3/4 inch run of conduit in case anyone ... addition) (conduit runs interior sub-panel will be interior). ...
    (alt.home.repair)
  • Re: Household sub-panel neutral isolated from ground
    ... at the sub-panel AND the neutral and ground are still short to each ... low voltage to put between a person and the dangerous voltage available within the system. ... At the point where the neutral is grounded, (bonded to the safety ground conductor) the impedance of the ground electrode must be low enough that expected current through this path do not produce dangerous safety ground conductor voltage with respect to local Earth. ... If the neutral conductor between the main panel and the were to become high resistance, and the ground and neutral were bonded at the sub-panel, Then the safety ground conductor at the sub-panel would be expected to have a voltage proportional to load current. ...
    (sci.electronics.design)
  • Re: splitting a circuit breaker into two?
    ... No two homes are done the same. ... I've been taking out conduit loops and just absolutely BIZARRE ... follow another conduit and wind up back at the panel. ... second floor bedroom, and piggybacked the second phase from *there*, the ...
    (rec.games.pinball)
  • Re: Electric Service Amps
    ... Typically this is done by a licensed electrician, ... >If the panel ought to be replaced is that a nightmare of replacing each ... >conduit from the panel to its first junction box or do they just try to do ...
    (alt.home.repair)
  • Re: splitting a circuit breaker into two?
    ... with electricity. ... No two homes are done the same. ... I've been taking out conduit loops and just absolutely BIZARRE ... follow another conduit and wind up back at the panel. ...
    (rec.games.pinball)