Re: Double Pole Circuit Breakers



On Fri, 23 Jun 2006 08:11:40 -0700, ~^Johnny^~
<nospam@xxxxxxxxxxxxxxxxx> wrote:

On Fri, 23 Jun 2006 13:22:41 GMT, spambait@xxxxxxxxxx (Doug Miller)
wrote:

100A at 240V -- and, as noted above, if only 120V loads are in use, the total
current draw is (up to) 200A at 120V.


The power consumption is equivalent to 200A at 120V,
but only 100A are flowing. Kirchoff's Law will not
be violated!

Currents in series do not add; =voltages= add.
It's still 100A at 240V.

Better yet,
Look at it this way: If I hang ten 12V lamps in series across a 120V
line, and each lamp is 120 watts, am I pulling a total of 100 amps?
I am not! I am drawing ten amps! Each lamp gets 12V at 10A. 100A
doesn't ever flow, anywhere in the circuit. But I'm still consuming
1200W: 120V at 10A, _NOT_ 12V at 100A. If the lamps were in
parallel, they would require 100A at 12V. But they're not. That's a
load calculation only.

An Edison circuit is just a 240 volt circuit with a grounded
center-tap. In theory, if loads are balanced, the neutral drops out
of the circuit, as the individial loads become a series-parallel
voltage divider network. Each load receives 120V at its rated =power=.



--
-john
wide-open at throttle dot info
.



Relevant Pages

  • Re: Double Pole Circuit Breakers
    ... I am drawing ten amps! ... load calculation only. ... An Edison circuit is just a 240 volt circuit with a grounded ... If the currents in each side are not equal then the current in the low side ...
    (alt.home.repair)
  • Re: Load capacity of 200-amp panel
    ... pretty basic principles of circuit analysis. ... carries the exact SAME current which is flowing in the other hot. ... IF it's supplying a 240V load, ... is a max of 200 amps. ...
    (alt.home.repair)
  • Re: Variable 60A load
    ... > Does anybody know how to build or where to buy a variable 60A load that I ... > can use to test household circuit breakers? ... source of high current - 60 amps is well possible. ...
    (sci.electronics.design)
  • Re: Bally Solenoid Driver Test Board
    ... in mind to properly test a solenoid circuit, ...  I had a lamp ... driver once that did not work 100% in my machine, ... and under a normal load would fail. ...
    (rec.games.pinball)
  • Re: Breaker size for oven
    ... This is often done with a small breaker box. ... Does that mean that, even on a circuit for a single appliance, ... the breaker size should be 1/.8 times the maximum expected load ... would handle a load of 14.2 amps multiplied by 1.25, ...
    (alt.home.repair)

Loading