Re: replacing older electrical outlets




volts500 wrote:
> grodenhiATgmailDOTcom wrote:
> > I'm not looking to take shortcuts and put safety at risk, Currently
> > half of the outlets are the older 2 prong variety (all in
> > kitchen/bath/livingroom are updated). We just have a few outlets in
> > hall ways and bedrooms that are older 2 prong still. the only devices
> > that get plugged into these are 2 prong devices likes vacuum, and the
> > laptops which are three prong (using an adaptor). We're repainting the
> > hallways and I was going to upgrade these outlets more for looks now
> > (to white outlets) and when money is less tight have them grounded.
> > I'm just wondering if there is risk (ie fire, etc) due to hooking 3
> > prong outlets to ungrounded box.
> >
> > We plan on grounding eventually. How big a job is this for experienced
> > electrician? The outlets are all on 1st floor of a ranch and the
> > finished basement below has suspended ceilings (ie access to flooring
> > above by moving tiles).
>
> NEC does allow 2 prong receptacles to be replaced with 3 prong
> receptacles _IF_ they are GFCI protected.
> What you need to do is find in first outlet in each circuit, then
> install a GFCI receptacle at that location, feeding the downstream
> receptacles through that GFCI receptacle. All the downstream
> receptacles can then be replaced with reguler 3 prong receptacles to
> meet NEC requirements. If line and load are not available at the
> first outlet, another soltion is to use GFCI breakers.

In addition, you should check and see whether you do in fact have a
ground wire that may just be connected to the metal junction boxes.
You probably have just 2-wire cable connecting all your outlets, but
there was a period where an undersized ground wire was included in the
cable and was simply twisted to the other ground wires and tied to the
box. Another variation was that the undersized ground wire was wrapped
around the outside of the cable sheath and the cable was clamped to the
box which would still nake a ground connection to the box. In this
case, it may not be readily apparent that there is in fact a ground
wire connected to anythig.

A quick way to see if there may be a ground would be to take the cover
plate off a duplex outlet, and use a neon light tester between the hot
side of the duplex and the metal box. If the tester lights, then you
probably have a ground wire. If this is the case, then write back here
for more instructions about what to do to actually hook up a ground to
a 3-prong duplex outlet.

But, you probably have no ground wire at all, and will need to either
add GFCI outlets like volts500 said, or else start fishing new cables.

Ken

.



Relevant Pages

  • Re: replacing older electrical outlets
    ... We just have a few outlets in ... > hall ways and bedrooms that are older 2 prong still. ... NEC does allow 2 prong receptacles to be replaced with 3 prong ... install a GFCI receptacle at that location, ...
    (alt.home.repair)
  • Re: Are the outlets on the same circuit?
    ... I have two outlets in the house which are not working. ... Open up the receptacles and check the connections. ... You might see a burn mark on one of the receptacles. ... Remove the wires from the receptacles and at one receptacle location connect the ground wire to the hot wire and go to the other receptacle location and check for continuity between the hot and ground wires. ...
    (alt.home.repair)
  • Re: radio works on DC but not AC
    ... > Try other outlets. ... If the radios do not work in other outlets, ... outlets have two power wires and one ground wire. ... Even if 3 prong, they can't for safety reasons use the Ground. ...
    (sci.electronics.repair)
  • Re: switching out 2 pin for 3 pin sockets in my victorian home
    ... victorian home and most of my appliances are 3 pin. ... ground terminal of the recep to a grounding screw tapped into the box. ... for new construction the ground wire must be ... whereas using grounded outlets without a ground wire is NOT ...
    (alt.home.repair)
  • Re: Electricians: I need your advice
    ... box with the use of a ground wire. ... if all the electric is run inside metal conduit. ... He says the 3 prong outlets will be changed to 2 ...
    (rec.games.pinball)