Re: Ground Rod For House ?



An example demonstrates the earthing problem. A 12 AWG wire
from wall receptacle maybe 50 feet back to mains box has less
than 0.2 ohms resistance. That same wire would have something
like 120 ohms impedance. Lets say a tiny 100 amp transient
seeks earth ground via that 50 foot wire. Therefore a wall
receptacle - and adjacent electronics - will be at something
less than 12,000 volts. Will that transient seek earth via
that safety ground wire? Of course not. It will also seek
other and destructive paths via adjacent electronics.

Wire length is but one reason why a wall receptacle safety
ground is not sufficient as earth ground. Also explains why
plug-in protectors are so ineffective.

Essential to minimizing wire impedance are wire length, no
sharp bends, and other characteristics cited previously. Also
important is a concept cited by Bud--
> Clamping all incoming wires to the same the same ground
> reference is the best way I know to protect electronics. ...
The quality of a service entrance protector is only as
effective as its earth ground which is why distance to that
earthing is so critical and why single point earthing is
essential. That means the 6 AWG wire does not go up over a
foundation and then down to an earth ground rod. That wire
goes through foundation somewhere just above the ground rod so
that wire distance is shorter with sharp bends eliminated.
Also important is that earthing wire remain separated from
other non-earthing wires to avoid induced transients.

Yes, lower resistance does help which is why high
reliability facilities such as electric substations expand
their earth ground to also lower resistance. It is also why
earthing should be planned when the footing are poured.
Equipotential being another aspect of superior earthing.

Unfortunately we still don't build as if the transistor
exists. We still do earthing as an afterthought. Effective
earthing addresses concepts in excess of that performed by
conventional household earthing. Equipotential being a
concept of transistor protection that is not as essential to
human protection. If we built buildings for effective
transistor protection, then Ufer grounds would be routine; and
not some afterthought to supplement water pipe ground such as
ground rods. Even water pipe would enter a building adjacent
to all other utilities to contribute to transistor safety.

Even NEC requires all incoming electrical utilities be
earthed to a common point for human safety - a problem still
found even in some new homes.

That 20 foot requirement from NEC is article 800.40(A)(4):
> Length. The primary protector grounding conductor shall
> be as short as practicable. In one- and two-family
> dwellings, the primary protector grounding conducutor
> shall be as short as practicable, not to exceed 6.0
> meters (20 ft) in length.

Same paragraphs is also found in Article 820.

Cinergy demonstrates how to solve earthing problems created
when utilities arrive at wrong locations. A problem often
created by service installers or builders who still have not
learned about proper earthing:
http://www.cinergy.com/surge/ttip08.htm

Concrete encased grounding (Ufer grounds) were so well
proven even before WWII as to even protect munitions from
direct lightning strikes. If water pipe earthing was so
effective, then why do they implement Ufer grounding even in
buildings with water pipe grounds? Halo grounds are but
another way of improved earthing.

Again, to answer the original poster's question - water pipe
earthing alone is no longer sufficient to meet code. Upgrade
to accomplish more than just meet code. Transistor protection
is only as effective as a building's earth ground.

Bud-- wrote:
> As I said protector blocks for cable and TV should be immediately
> adjacent to the panel so all wiring is clamped to the same ground
> reference. You don't explain how a ground rod would help in this
> instance. Adding a ground rod near the FAX is not going to provide
> a low impedance to keep the ground reference for the FAX the same
> as the incoming neutral.
> ...
>
> Incoming utilities listed have to have protector blocks near the power
> panel to get a common grounding reference.
>
> How does a 10 foot wire to a high resistance ground rod provide a lower
> ground impedance than a grounding electrode conductor and water pipe?
> This is cental to your arguments. Perhaps you could explain and also
> provide some citations that support your view.
>
> For a 500A service the conductor to a ground rod has to be #6. The
> conductor to a water pipe has to be 2/0 - 3.5 x the area. How come?
> Surges include high frequency components for which impedance is
> important. Grounding electrode conductor and water pipe has one
> function of limiting surges.
>
>> Another problem with using a cold water pipe as an earth
>> ground connection - code wants each utility to be earthed less
>> than 20 feet to the common point.
>
> Cite the code.
> ...
>
> Clamping all incoming wires to the same the same ground reference
> is the best way I know to protect electronics. That requires the
> protector blocks to be near the electrical panel. (More properly
> thay have to be near each other.) That is likely a lot more
> important than resistance or impedance to ground. If all wiring
> was clamped to the same reference with no ground connection could
> electronics see a difference.
>
> > Gfretwell has posted how homes are now being built so as to
> > provide superior transistor safety in pictures at:
> > http://members.aol.com/gfretwell/ufer.jpg
> >
> This is a concrete encased electrode which I said is probably the second
> best electrode (after water pipes). It is one of 3 electrodes that must
> be included in a ground system, if present. (The other 2 are water pipe
> and building steel, which a home doesn't have.) Not included: ground rod.
>
> > Another also demonstrates better earthing. None of this
> > would be required if city water pipe was sufficient as earth
> > ground for transistor safety:
> > http://www.knology.net/~res0958z/
> >
> Most of us don't put 55 foot high lightning rods in our back yard. Not
> particualrly relevant.
>
> -------------
> With regard to: Bud-- does not even quote code to justify his post. You
> do not understand why water pipes are required to have a SUPPLEMENTAL
> electrode and don't listen to people who do understand. Since arguing
> the code is pointles, I tried Physics - ground resistance. That doesn't
> seem to work either.
>
> bud--
.



Relevant Pages

  • Re: Repairing Lightning Damaged Tvs
    ... > Establish the single point earth ground. ... > be a buried bare 4 AWG ground wire that interconnects AC ... > not connect to any other earthing wire until they all meet at ... > protector must connect from each wire to that bus bar. ...
    (sci.electronics.repair)
  • Re: Building Ground (long-...sorry)
    ... The cow is killed. ... The concept is called single point earthing. ... Connecting phone line with a 20' plus ground wire or via pipes ... A protector only connects from AC electric ...
    (sci.electronics.repair)
  • Re: Ground Rod For House ?
    ... An example demonstrates the earthing problem. ... That same wire would have something ... other and destructive paths via adjacent electronics. ... The quality of a service entrance protector is only as ...
    (alt.home.repair)
  • Re: surge protectors
    ... 40 annually to the WTC - and electronics not ... this is about a nearby lightning strike to a long wire antenna. ... You did not see protector devices inside the blender? ... As described in another post is wire impedance. ...
    (alt.home.repair)
  • Re: Daisy chain wireless routers
    ... Every wire is earthed to the same earth ground. ... via a surge protector for twisted pair. ... The protector is only as effective as its earth ground. ... A protector adjacent to electronics (and too far from ...
    (uk.telecom.broadband)